Basic Electrical and Electronics Engineering: Unit II: Electrical Machines

Transformer Tests (Open, Short-circuit test)

Single Phase Transformer

Performance of a transformer can be calculated on the basis of its equivalent circuit which contains four main parameter, the equivalent resistance 'Ro1' as referred to primary and 'Ro2' referred as secondary

TRANSFORMER TESTS

Performance of a transformer can be calculated on the basis of its equivalent circuit which contains four main parameter, the equivalent resistance 'Ro1' as referred to primary and 'Ro2' referred as secondary, the equivalent leakage reactance Xo1, Xo2 as referred to primary and secondary respectively, the core loss conductors G0 and the magnetizing susceptance Bo.

These constants (or) parameters can be easily determined by two tests.

(i) Open-circuit test

(ii) Short-circuit test

These tests are very economical and convenient, because they required information without actually loading the transformer.

3.3.8.1 Open Circuit Test (or) No-Load Test (OC Test)

The purpose of this test is to determine no-load loss (or) core loss and no-load I0 which is useful in finding Xo and Ro.


The transformer primary is connected to AC supply through ammeter, wattmeter. The secondary of transformer kept open. Usually low voltage side is called as primary and high voltage side is called as secondary.

The primary is excited by rated voltage, the wattmeter measured input power. The armature measures input curved and voltmeter gives the applied primary voltage.

As transformer secondary is open, it is on load so current drawn by the primary is no load current Io. The two components of the no load current are

Im = Io sin ϕo

Ic = Io cos ϕo

where cos ϕo = no load power factor and hence power input can be written as

Wo = VoIo cos ϕo

As secondary is open I2 = 0. Thus its reflected current on primary is also zero. So primary current I1 = I0. The transformer no load current is always very small, handly 2 to 4% of its fall load value.


Total copper losses in OC test are negligibly small. As output power is zero and copper losses are very low, the total input power is used to supply iron losses. This power is measured by the wattmeter (ω0). Hence the wattmeter in OC test gives iron losses which remain constant for all the loads.

ωo = Pi = iron losses

ωo = Wo/VoIo cos Ɵ

cos Ɵo = Wo/VoIo (No load power factor)

The value of cos Ɵ0 is known then we can obtain,

Ic = Im cos Ɵo

Im = Io sin Ɵo

The we determine the circuit parameters

Ro = Vo/Ic and Xo = Vo/Im

3.3.8.2 Short Circuit Test (SC Test)


The fig shows the short circuit testing of transformer. The secondary is short circuited with the help of thick copper wire (or) solid link. As secondary is shorted, its resistance is very small and on rated voltage it may draw very large current. Such large current can cause over heating and burning of the transformer. To limit this short circuit current, primary is enough to cause rated current to flow through primary which can be observed on ammeter. Voltage applied is low which is a small fraction of the rated voltage. The iron losses are function of applied voltage so the iron losses in reduced voltage test are very small. Hence wattmeter reading is the power loss which is equal to full load copper losses as iron losses are very low.

Wsc = (Pcu) F.L

Wsc = Vsc Isc cos Ɵsc

cos Ɵsc = Wsc/ VscIco

Wsc = Isc2 Rle

Rle = Wsc/Isc2

Zle = Vse/Ise = √Rle2 + Xle2

Xle = √Zle2 - Rle2

Thus we get the equivated circuit parameters Rle, Xle and Zle.

Example: 20

A 220/440 V single phase transformer has the following test results

OC test: 230 V, 1 A, 60 watts, LV side

SC test: 18 V, 18 A, 80 watts, HV side

Obtain the equivalent circuit parameters of transformer refered to LV side.

Solution:

OC test:

Vo = 220 V, Io = 1A, Wo = 60 W

Wo = VoIo cos Ɵo

No-load input power factor cos Ɵo = Wo/VoIo

= 60 / 220×1

cos Ɵo = 0.27

sin Ɵo = 0.961

Ic = Io cos Ɵo

= 1 × 0.27

Ic = 0.27

Ro = Vo/Iw = 220/0.27

Ro = 814 Ω

Im = Io sin Ɵo

= 1 × 0.961

Im = 0.961

Xo = Vo/Im = 220/0.961

Xo = 228.92

SC test

Ic = 0.27 Ro = 814Ω

Im = 0.96 Xo = 228.92 Ω

SC voltage Vsc = 18 V

SC current Isc = 18 A

SC power Wsc = 80 W

Zo2 = Vsc/Isc = 18/18 = 1Ω

Wsc = Isc2 Ro2

Ro2 = Wsc/Isc2 = 80/(18)2 = 0.246Ω

Transformation ratio K = V2/V1 = 440/220 = 2

Zol = Zo2/K2 = 1/22

= 0.25 Ω

Ro1 = Ro2/K2 = 0.246/22 = 0.0617 Ω

Xo1 = √ZA2 - Ro12

= √(0.25)2- (0.0617)2

Xo1 = 0.242 Ω

Basic Electrical and Electronics Engineering: Unit II: Electrical Machines : Tag: : Single Phase Transformer - Transformer Tests (Open, Short-circuit test)