Basic Electrical and Electronics Engineering: Unit II: Electrical Machines

Three Phase Transformer Star and Delta Configurations

A three phase transformer has three sets of primary and secondary windings.

THREE PHASE TRANSFORMER STAR AND DELTA CONFIGURATIONS

A three phase transformer has three sets of primary and secondary windings. Depending upon the windings are interconnection, determines whether the connection is a star or delta configuration.

The three available voltages, which themselves are each displaced from the other by 120 electrical degrees

With three single-phase transformers connected together, the magnetic flux's in the three transformers differ in phase by 120 time-degrees. With a single the three-phase transformer there are three magnetic flux's in the core differing in time-phase by 120 degrees.

Transformer Star and Delta Configurations

Symbols are generally used on a three phase transformer to indicate the type or types of connections used with upper case Y for star connected, D for delta connected and Z for interconnected star primary windings, with lower case y, d and z for their respective secondaries. Then, Star-Star would be labelled Yy, Delta-Delta would be labelled Dd and interconnected star to interconnected star would be Zz for the same types of connected transformers.


Transformer Winding Identification


In which three single-phase transformers may be connected together between their primary and secondary three-phase circuits. These four standard configurations are given as: Delta-Delta (Dd), Star-Star (Yy), Star-Delta (Yd), and Delta-Star (Dy).

Transformers for high voltage operation with the star connections has the advantage of reducing the voltage on an individual transformer, reducing the number of turns required and an increase in the size of the conductors, making the coil windings easier and cheaper to insulate than delta transformers.

The delta-delta connection nevertheless has one big advantage over the star-delta configuration, in that if one transformer of a group of three should become faulty or disabled, the two remaining ones will continue to deliver three-phase power with a capacity equal to approximately two thirds of the original output from the transformer unit.

Transformer Delta and Delta Connections


In a delta connected (Dd) group of transformers, the line voltage, VL is equal to the supply voltage, VL = VS. But the current in each phase winding is given as: 1/√3 × IL of the line current, where IL is the line current.

One disadvantage of delta connected three phase transformers is that each transformer must be wound for the full-line voltage, (in our example above 100V) and for 57.7 per cent, line current. The greater number of turns in the winding, together with the insulation between turns, necessitate a larger and more expensive coil than the star connection. Another disadvantage with delta connected three phase transformers is that there is no "neutral" or common connection.

In the star-star arrangement (Yy), (wye-wye), each transformer has one terminal connected to a common junction, or neutral point with the three remaining ends of the primary windings connected to the three-phase mains supply. The number of turns in a transformer winding for star connection is 57.7 per cent, of that required for delta connection.

The star connection requires the use of three transformers, and if any one transformer becomes fault or disabled, the whole group might become disabled. Nevertheless, the star connected three phase transformer is especially convenient and economical in electrical power distributing systems, in that a fourth wire may be connected as a neutral point, (n) of the three star connected secondaries as shown

Transformer Star and Star Connections


The voltage between any line of the three-phase transformer is called the "line voltage", VL, while the voltage between any line and the neutral point of a star connected transformer is called the "phase voltage", Vp. This phase voltage between the neutral point and any one of the line connections is 1/√3 × VL of the line voltage.

Then above, the primary side phase voltage, Vp is given as.

V = 1/√3 × VL

The secondary current in each phase of a star-connected group of transformers is the same as that for the line current of the supply, then IL = IS.

Then the relationship between line and phase voltages and currents in a three- phase system can be summarised as: